When the power factor is unity (cosφ = 1), which statement about reactive power Q is true?

Get ready for the EPE301C Course 1 Test with our extensive quiz. Study using flashcards and multiple-choice questions, complete with hints and explanations. Ace your exam with confidence!

Multiple Choice

When the power factor is unity (cosφ = 1), which statement about reactive power Q is true?

Explanation:
Unity power factor means the voltage and current are in phase, so there is no reactive power. Reactive power Q comes from a phase difference between voltage and current, and when φ = 0 degrees (cosφ = 1), the sine part is zero. In RMS terms, Q = VI sinφ, which becomes zero, while real power is P = VI cosφ = VI and apparent power is S = VI. So P equals S and Q equals zero. The other statements would require a phase angle different from zero (for example, Q being maximal would need a 90-degree phase shift, which is not the case here), so the correct takeaway is that reactive power is zero when the power factor is unity.

Unity power factor means the voltage and current are in phase, so there is no reactive power. Reactive power Q comes from a phase difference between voltage and current, and when φ = 0 degrees (cosφ = 1), the sine part is zero. In RMS terms, Q = VI sinφ, which becomes zero, while real power is P = VI cosφ = VI and apparent power is S = VI. So P equals S and Q equals zero. The other statements would require a phase angle different from zero (for example, Q being maximal would need a 90-degree phase shift, which is not the case here), so the correct takeaway is that reactive power is zero when the power factor is unity.